{"id":40950,"date":"2026-01-26T09:58:08","date_gmt":"2026-01-26T14:58:08","guid":{"rendered":"https:\/\/www.dmcinfo.com\/?p=40950"},"modified":"2026-01-19T18:38:02","modified_gmt":"2026-01-19T23:38:02","slug":"data-center-construction-how-are-you-testing-your-power-systems","status":"publish","type":"post","link":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/","title":{"rendered":"Data Center Construction: How Are You Testing Your Power Systems?"},"content":{"rendered":"\n<p>Data centers are the backbone of our digital economy. As construction projects surge to meet growing demand, a critical question often goes unasked: How are you testing your power systems, and are you doing enough?\u00a0<\/p>\n\n\n\n<p>When it comes to reliability, every\u00a0component\u00a0in your power infrastructure matters. UPS systems, battery backups, switchgear, and backup generators all play a role in keeping operations online. But\u00a0here\u2019s\u00a0the catch: testing individual components\u00a0isn\u2019t\u00a0the same as testing the entire system. Each piece can pass its own validation, yet the integrated system may still fail under real-world conditions. Failure modes often\u00a0emerge\u00a0only when these components interact\u00a0under load, during transitions, or in response to unexpected events.<\/p>\n\n\n\n<h2 class=\"wp-block-heading\" id=\"h-why-testing-matters\">Why Testing Matters\u00a0<\/h2>\n\n\n\n<p>Downtime in a data center is costly and sometimes catastrophic. Power systems are complex, and their performance under stress\u00a0determines\u00a0whether your facility can\u00a0deliver on\u00a0its uptime promises. Yet many projects rely on manual checks or incomplete testing strategies that leave gaps.\u00a0\u00a0<\/p>\n\n\n\n<p>Consider these questions:\u00a0<\/p>\n\n\n\n<ul class=\"wp-block-list\">\n<li>Are your UPS systems\u00a0validated\u00a0for transient response during failover?\u00a0<\/li>\n\n\n\n<li>Has your switchgear been tested under realistic load conditions?\u00a0<\/li>\n\n\n\n<li>Do your backup generators respond correctly during commissioning?\u00a0<\/li>\n\n\n\n<li>Is your battery management system (BMS) ready for real-world charge\/discharge cycles?\u00a0<\/li>\n<\/ul>\n\n\n\n<p>If\u00a0you\u2019re\u00a0not confident in the answers,\u00a0you\u2019re\u00a0not alone. Many teams assume that OEM testing or basic commissioning is enough. It\u00a0probably isn\u2019t.\u00a0<\/p>\n\n\n\n<h2 class=\"wp-block-heading\" id=\"h-where-testing-should-happen-nbsp\">Where Testing Should Happen&nbsp;<\/h2>\n\n\n\n<p>Comprehensive testing should occur at multiple stages:&nbsp;<\/p>\n\n\n\n<ul class=\"wp-block-list\">\n<li><strong>Factory Acceptance Testing (FAT)<\/strong>\u00a0\u2013 Validate performance before equipment leaves the OEM\u00a0<\/li>\n\n\n\n<li><strong>On-Site Commissioning<\/strong>\u00a0\u2013 Confirm integrated system behavior under real-world conditions<\/li>\n\n\n\n<li><strong>Production Testing for OEMs<\/strong>\u00a0\u2013 Ensure every unit meets specifications before shipment<\/li>\n<\/ul>\n\n\n\n<p>Key subsystems to focus on:\u00a0<\/p>\n\n\n\n<ul class=\"wp-block-list\">\n<li><strong>UPS and Battery Backup Systems<\/strong>\u00a0\u2013 Runtime validation, transient response, and BMS functionality\u00a0<\/li>\n\n\n\n<li><strong>Switchgear and Power Distribution<\/strong>\u00a0\u2013 Failover logic and power quality under dynamic loads<\/li>\n\n\n\n<li><strong>Backup Generators<\/strong>\u00a0\u2013 Load simulation and response monitoring during commissioning\u00a0<\/li>\n\n\n\n<li><strong>Energy Storage Systems<\/strong>\u00a0\u2013 Charge\/discharge cycles and safety interlocks<\/li>\n<\/ul>\n\n\n\n<figure class=\"wp-block-image size-full\"><img decoding=\"async\" width=\"900\" height=\"506\" src=\"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19094858\/power-system-testing.jpg\" alt=\"Diagram of data center power system testing\" class=\"wp-image-40963\" srcset=\"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19094858\/power-system-testing.jpg 900w, https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19094858\/power-system-testing-300x169.jpg 300w, https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19094858\/power-system-testing-768x432.jpg 768w\" sizes=\"(max-width: 900px) 100vw, 900px\" \/><\/figure>\n\n\n\n<h2 class=\"wp-block-heading\" id=\"h-the-better-way-nbsp\">The Better Way&nbsp;<\/h2>\n\n\n\n<p>DMC brings decades of experience testing DC power systems for the automotive and aerospace industries, where reliability is non-negotiable. We apply that\u00a0expertise\u00a0to data center DC and AC power infrastructure with\u00a0automated test solutions\u00a0that:\u00a0<\/p>\n\n\n\n<ul class=\"wp-block-list\">\n<li>Execute custom or standard test scripts<\/li>\n\n\n\n<li>Control\u00a0load banks to simulate real-world conditions<\/li>\n\n\n\n<li>Monitor power quality and transient response<\/li>\n\n\n\n<li>Log and report\u00a0results\u00a0for compliance and traceability<\/li>\n<\/ul>\n\n\n\n<p>DMC excels at\u00a0thinking outside the box<strong>.<\/strong>\u00a0It&#8217;s what sets us apart. We\u00a0don\u2019t\u00a0just deliver cookie-cutter solutions; we design and integrate unique systems tailored to your requirements and challenges. Whether you need a turnkey test station or a creative approach to integrate with existing equipment,\u00a0we\u2019ll\u00a0find a way to make it work.\u00a0<\/p>\n\n\n\n<h2 class=\"wp-block-heading\" id=\"h-component-level-testing-nbsp\">Component-Level Testing&nbsp;<\/h2>\n\n\n\n<p>Before you can trust the entire system, you need confidence in its building blocks. Component-level testing ensures that each UPS, battery module, switchgear panel, and generator meets its specifications under controlled conditions. This step verifies:&nbsp;<\/p>\n\n\n\n<ul class=\"wp-block-list\">\n<li>Electrical performance and safety compliance\u00a0<\/li>\n\n\n\n<li>Firmware and control logic functionality<\/li>\n\n\n\n<li>Proper response to simulated faults and load changes<\/li>\n<\/ul>\n\n\n\n<p>Component\u00a0testing is essential for quality assurance and regulatory compliance, but\u00a0it\u2019s\u00a0only the first step. Even when every\u00a0component\u00a0passes, integration can introduce new failure modes.\u00a0That\u2019s\u00a0why system-level testing\u00a0is equally\u00a0critical.\u00a0<\/p>\n\n\n\n<h2 class=\"wp-block-heading\" id=\"h-system-level-testing-nbsp\">System-Level Testing&nbsp;<\/h2>\n\n\n\n<p>Component-level testing\u00a0ensures\u00a0each part works as intended. But data centers\u00a0operate\u00a0as\u00a0complex systems, and failures often occur at the interfaces:\u00a0<\/p>\n\n\n\n<ul class=\"wp-block-list\">\n<li>UPS and generators may not synchronize during transfer\u00a0<\/li>\n\n\n\n<li>Switchgear logic may falter under simultaneous load changes\u00a0<\/li>\n\n\n\n<li>Battery systems may behave unpredictably during extended outages<\/li>\n<\/ul>\n\n\n\n<p>System-level testing replicates these scenarios before they happen in production, saving time, money, and reputation.\u00a0<\/p>\n\n\n\n<h2 class=\"wp-block-heading\" id=\"h-further-reading\">Further Reading\u00a0<\/h2>\n\n\n\n<ul class=\"wp-block-list\">\n<li><a href=\"https:\/\/www.dmcinfo.com\/our-work\/automated-testing-of-a-mobile-energy-storage-system\/\">Automated Testing of a Mobile Energy Storage System<\/a><\/li>\n\n\n\n<li><a href=\"https:\/\/www.dmcinfo.com\/our-work\/smart-energy-amp-solution\/\">Smart Energy AMP Solution<\/a><\/li>\n\n\n\n<li><a href=\"https:\/\/www.dmcinfo.com\/our-work\/battery-testing-with-large-scale-distributed-platform\/\">Battery Testing with Large Scale Distributed Platform<\/a><\/li>\n\n\n\n<li><a href=\"https:\/\/www.dmcinfo.com\/blog\/16035\/dmc-joins-strategic-partnership-with-battery-innovation-center\/\">DMC Joins Strategic Partnership with Battery Innovation Center<\/a><\/li>\n<\/ul>\n\n\n\n<h2 class=\"wp-block-heading\" id=\"h-let-s-nbsp-start-the-conversation-nbsp\">Let\u2019s&nbsp;Start the Conversation&nbsp;<\/h2>\n\n\n\n<p>Data center reliability starts with rigorous testing. If&nbsp;you\u2019re&nbsp;asking:&nbsp;<\/p>\n\n\n\n<ul class=\"wp-block-list\">\n<li>Who\u2019s\u00a0doing this testing?\u00a0<\/li>\n\n\n\n<li>How are we testing?\u00a0<\/li>\n\n\n\n<li>Is there a better way?\u00a0<\/li>\n<\/ul>\n\n\n\n<p>The answer is\u00a0yes;\u00a0there is a better way.\u00a0Let\u2019s\u00a0talk about how DMC can help you\u00a0validate\u00a0every critical subsystem and the entire power system before it goes live.\u00a0<\/p>\n\n\n\n<p><strong><a href=\"https:\/\/www.dmcinfo.com\/contact\/\">Contact us today<\/a>\u00a0and\u00a0let\u2019s\u00a0discuss your data center power\u00a0component\u00a0and system-level testing challenges.\u00a0<\/strong><\/p>\n","protected":false},"excerpt":{"rendered":"<p>Data centers are the backbone of our digital economy. As construction projects surge to meet growing demand, a critical question often goes unasked: How are you testing your power systems, and are you doing enough?\u00a0 When it comes to reliability, every\u00a0component\u00a0in your power infrastructure matters. UPS systems, battery backups, switchgear, and backup generators all play [&hellip;]<\/p>\n","protected":false},"author":72,"featured_media":40966,"comment_status":"closed","ping_status":"open","sticky":false,"template":"","format":"standard","meta":{"footnotes":""},"categories":[730],"tags":[],"class_list":["post-40950","post","type-post","status-publish","format-standard","has-post-thumbnail","hentry","category-test-and-measurement-automation"],"yoast_head":"<title>Data Center Construction: How Are You Testing Your Power Systems? | DMC, Inc.<\/title>\n<meta name=\"description\" content=\"How are you testing your data center power systems? Learn why testing matters and where it should happen in this guide by DMC, Inc.\" \/>\n<meta name=\"robots\" content=\"index, follow, max-snippet:-1, max-image-preview:large, max-video-preview:-1\" \/>\n<link rel=\"canonical\" href=\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/\" \/>\n<meta property=\"og:locale\" content=\"en_US\" \/>\n<meta property=\"og:type\" content=\"article\" \/>\n<meta property=\"og:title\" content=\"Data Center Construction: How Are You Testing Your Power Systems?\" \/>\n<meta property=\"og:description\" content=\"How are you testing your data center power systems? Learn why testing matters and where it should happen in this guide by DMC, Inc.\" \/>\n<meta property=\"og:url\" content=\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/\" \/>\n<meta property=\"og:site_name\" content=\"DMC, Inc.\" \/>\n<meta property=\"article:publisher\" content=\"https:\/\/www.facebook.com\/pages\/DMC-Inc\/107982009242929\" \/>\n<meta property=\"article:published_time\" content=\"2026-01-26T14:58:08+00:00\" \/>\n<meta property=\"og:image\" content=\"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg\" \/>\n\t<meta property=\"og:image:width\" content=\"1536\" \/>\n\t<meta property=\"og:image:height\" content=\"658\" \/>\n\t<meta property=\"og:image:type\" content=\"image\/jpeg\" \/>\n<meta name=\"author\" content=\"Brent Hoerman\" \/>\n<meta name=\"twitter:card\" content=\"summary_large_image\" \/>\n<meta name=\"twitter:label1\" content=\"Written by\" \/>\n\t<meta name=\"twitter:data1\" content=\"Brent Hoerman\" \/>\n\t<meta name=\"twitter:label2\" content=\"Est. reading time\" \/>\n\t<meta name=\"twitter:data2\" content=\"4 minutes\" \/>\n<script type=\"application\/ld+json\" class=\"yoast-schema-graph\">{\"@context\":\"https:\/\/schema.org\",\"@graph\":[{\"@type\":\"Article\",\"@id\":\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#article\",\"isPartOf\":{\"@id\":\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/\"},\"author\":{\"name\":\"Brent Hoerman\",\"@id\":\"https:\/\/www.dmcinfo.com\/#\/schema\/person\/ee80b953fd0e83c3083528f88968aecc\"},\"headline\":\"Data Center Construction: How Are You Testing Your Power Systems?\",\"datePublished\":\"2026-01-26T14:58:08+00:00\",\"mainEntityOfPage\":{\"@id\":\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/\"},\"wordCount\":724,\"publisher\":{\"@id\":\"https:\/\/www.dmcinfo.com\/#organization\"},\"image\":{\"@id\":\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#primaryimage\"},\"thumbnailUrl\":\"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg\",\"articleSection\":[\"Test and Measurement Automation\"],\"inLanguage\":\"en-US\"},{\"@type\":\"WebPage\",\"@id\":\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/\",\"url\":\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/\",\"name\":\"Data Center Construction: How Are You Testing Your Power Systems? | DMC, Inc.\",\"isPartOf\":{\"@id\":\"https:\/\/www.dmcinfo.com\/#website\"},\"primaryImageOfPage\":{\"@id\":\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#primaryimage\"},\"image\":{\"@id\":\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#primaryimage\"},\"thumbnailUrl\":\"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg\",\"datePublished\":\"2026-01-26T14:58:08+00:00\",\"description\":\"How are you testing your data center power systems? Learn why testing matters and where it should happen in this guide by DMC, Inc.\",\"inLanguage\":\"en-US\",\"potentialAction\":[{\"@type\":\"ReadAction\",\"target\":[\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/\"]}]},{\"@type\":\"ImageObject\",\"inLanguage\":\"en-US\",\"@id\":\"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#primaryimage\",\"url\":\"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg\",\"contentUrl\":\"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg\",\"width\":1536,\"height\":658,\"caption\":\"Engineer testing a data center on laptop\"},{\"@type\":\"WebSite\",\"@id\":\"https:\/\/www.dmcinfo.com\/#website\",\"url\":\"https:\/\/www.dmcinfo.com\/\",\"name\":\"DMC, Inc.\",\"description\":\"\",\"publisher\":{\"@id\":\"https:\/\/www.dmcinfo.com\/#organization\"},\"potentialAction\":[{\"@type\":\"SearchAction\",\"target\":{\"@type\":\"EntryPoint\",\"urlTemplate\":\"https:\/\/www.dmcinfo.com\/?s={search_term_string}\"},\"query-input\":{\"@type\":\"PropertyValueSpecification\",\"valueRequired\":true,\"valueName\":\"search_term_string\"}}],\"inLanguage\":\"en-US\"},{\"@type\":\"Organization\",\"@id\":\"https:\/\/www.dmcinfo.com\/#organization\",\"name\":\"DMC, Inc.\",\"url\":\"https:\/\/www.dmcinfo.com\/\",\"logo\":{\"@type\":\"ImageObject\",\"inLanguage\":\"en-US\",\"@id\":\"https:\/\/www.dmcinfo.com\/#\/schema\/logo\/image\/\",\"url\":\"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2025\/05\/27171146\/dmc-logo-1.png\",\"contentUrl\":\"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2025\/05\/27171146\/dmc-logo-1.png\",\"width\":418,\"height\":167,\"caption\":\"DMC, Inc.\"},\"image\":{\"@id\":\"https:\/\/www.dmcinfo.com\/#\/schema\/logo\/image\/\"},\"sameAs\":[\"https:\/\/www.facebook.com\/pages\/DMC-Inc\/107982009242929\",\"https:\/\/www.instagram.com\/dmcengineering\",\"https:\/\/www.youtube.com\/DMCEngineering\",\"https:\/\/www.linkedin.com\/company\/dmc-engineering\"]},{\"@type\":\"Person\",\"@id\":\"https:\/\/www.dmcinfo.com\/#\/schema\/person\/ee80b953fd0e83c3083528f88968aecc\",\"name\":\"Brent Hoerman\",\"image\":{\"@type\":\"ImageObject\",\"inLanguage\":\"en-US\",\"@id\":\"https:\/\/www.dmcinfo.com\/#\/schema\/person\/image\/\",\"url\":\"\/\/www.dmcinfo.com\/wp-content\/uploads\/wpo365\/profile-images\/72.png\",\"contentUrl\":\"\/\/www.dmcinfo.com\/wp-content\/uploads\/wpo365\/profile-images\/72.png\",\"caption\":\"Brent Hoerman\"},\"url\":\"https:\/\/www.dmcinfo.com\/blog\/author\/brenth\/\"}]}<\/script>","yoast_head_json":{"title":"Data Center Construction: How Are You Testing Your Power Systems? | DMC, Inc.","description":"How are you testing your data center power systems? Learn why testing matters and where it should happen in this guide by DMC, Inc.","robots":{"index":"index","follow":"follow","max-snippet":"max-snippet:-1","max-image-preview":"max-image-preview:large","max-video-preview":"max-video-preview:-1"},"canonical":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/","og_locale":"en_US","og_type":"article","og_title":"Data Center Construction: How Are You Testing Your Power Systems?","og_description":"How are you testing your data center power systems? Learn why testing matters and where it should happen in this guide by DMC, Inc.","og_url":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/","og_site_name":"DMC, Inc.","article_publisher":"https:\/\/www.facebook.com\/pages\/DMC-Inc\/107982009242929","article_published_time":"2026-01-26T14:58:08+00:00","og_image":[{"width":1536,"height":658,"url":"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg","type":"image\/jpeg"}],"author":"Brent Hoerman","twitter_card":"summary_large_image","twitter_misc":{"Written by":"Brent Hoerman","Est. reading time":"4 minutes"},"schema":{"@context":"https:\/\/schema.org","@graph":[{"@type":"Article","@id":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#article","isPartOf":{"@id":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/"},"author":{"name":"Brent Hoerman","@id":"https:\/\/www.dmcinfo.com\/#\/schema\/person\/ee80b953fd0e83c3083528f88968aecc"},"headline":"Data Center Construction: How Are You Testing Your Power Systems?","datePublished":"2026-01-26T14:58:08+00:00","mainEntityOfPage":{"@id":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/"},"wordCount":724,"publisher":{"@id":"https:\/\/www.dmcinfo.com\/#organization"},"image":{"@id":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#primaryimage"},"thumbnailUrl":"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg","articleSection":["Test and Measurement Automation"],"inLanguage":"en-US"},{"@type":"WebPage","@id":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/","url":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/","name":"Data Center Construction: How Are You Testing Your Power Systems? | DMC, Inc.","isPartOf":{"@id":"https:\/\/www.dmcinfo.com\/#website"},"primaryImageOfPage":{"@id":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#primaryimage"},"image":{"@id":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#primaryimage"},"thumbnailUrl":"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg","datePublished":"2026-01-26T14:58:08+00:00","description":"How are you testing your data center power systems? Learn why testing matters and where it should happen in this guide by DMC, Inc.","inLanguage":"en-US","potentialAction":[{"@type":"ReadAction","target":["https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/"]}]},{"@type":"ImageObject","inLanguage":"en-US","@id":"https:\/\/www.dmcinfo.com\/blog\/40950\/data-center-construction-how-are-you-testing-your-power-systems\/#primaryimage","url":"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg","contentUrl":"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2026\/01\/19095618\/data-center-power-systems.jpg","width":1536,"height":658,"caption":"Engineer testing a data center on laptop"},{"@type":"WebSite","@id":"https:\/\/www.dmcinfo.com\/#website","url":"https:\/\/www.dmcinfo.com\/","name":"DMC, Inc.","description":"","publisher":{"@id":"https:\/\/www.dmcinfo.com\/#organization"},"potentialAction":[{"@type":"SearchAction","target":{"@type":"EntryPoint","urlTemplate":"https:\/\/www.dmcinfo.com\/?s={search_term_string}"},"query-input":{"@type":"PropertyValueSpecification","valueRequired":true,"valueName":"search_term_string"}}],"inLanguage":"en-US"},{"@type":"Organization","@id":"https:\/\/www.dmcinfo.com\/#organization","name":"DMC, Inc.","url":"https:\/\/www.dmcinfo.com\/","logo":{"@type":"ImageObject","inLanguage":"en-US","@id":"https:\/\/www.dmcinfo.com\/#\/schema\/logo\/image\/","url":"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2025\/05\/27171146\/dmc-logo-1.png","contentUrl":"https:\/\/cdn.dmcinfo.com\/wp-content\/uploads\/2025\/05\/27171146\/dmc-logo-1.png","width":418,"height":167,"caption":"DMC, Inc."},"image":{"@id":"https:\/\/www.dmcinfo.com\/#\/schema\/logo\/image\/"},"sameAs":["https:\/\/www.facebook.com\/pages\/DMC-Inc\/107982009242929","https:\/\/www.instagram.com\/dmcengineering","https:\/\/www.youtube.com\/DMCEngineering","https:\/\/www.linkedin.com\/company\/dmc-engineering"]},{"@type":"Person","@id":"https:\/\/www.dmcinfo.com\/#\/schema\/person\/ee80b953fd0e83c3083528f88968aecc","name":"Brent Hoerman","image":{"@type":"ImageObject","inLanguage":"en-US","@id":"https:\/\/www.dmcinfo.com\/#\/schema\/person\/image\/","url":"\/\/www.dmcinfo.com\/wp-content\/uploads\/wpo365\/profile-images\/72.png","contentUrl":"\/\/www.dmcinfo.com\/wp-content\/uploads\/wpo365\/profile-images\/72.png","caption":"Brent Hoerman"},"url":"https:\/\/www.dmcinfo.com\/blog\/author\/brenth\/"}]}},"_links":{"self":[{"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/posts\/40950","targetHints":{"allow":["GET"]}}],"collection":[{"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/posts"}],"about":[{"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/types\/post"}],"author":[{"embeddable":true,"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/users\/72"}],"replies":[{"embeddable":true,"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/comments?post=40950"}],"version-history":[{"count":10,"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/posts\/40950\/revisions"}],"predecessor-version":[{"id":40968,"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/posts\/40950\/revisions\/40968"}],"wp:featuredmedia":[{"embeddable":true,"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/media\/40966"}],"wp:attachment":[{"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/media?parent=40950"}],"wp:term":[{"taxonomy":"category","embeddable":true,"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/categories?post=40950"},{"taxonomy":"post_tag","embeddable":true,"href":"https:\/\/www.dmcinfo.com\/wp-json\/wp\/v2\/tags?post=40950"}],"curies":[{"name":"wp","href":"https:\/\/api.w.org\/{rel}","templated":true}]}}